BRE did some testing on concealed space sprinklers and RTI
https://www.bre.co.uk/page.jsp?id=723
From part 5
AP Standard pendent, glass bulb 27.8
BR Recessed (at maximum recess distance), glass bulb 42.4
EC Concealed, domed concealer plate, glass bulb 71.9
CC Concealed, domed concealer plate, glass bulb 104.1
FC Concealed, flat plate, drop down deflector, fusible link, no vent holes 114.9
GC Concealed, flat plate, drop down deflector, fusible link 130.1
DC Concealed, flat plate, drop down deflector, fusible link 284.3
It is also interesting to see what effects poor installation will have to our assumptions on performance
Frame arms ‘normal’, minimum recess distance, favourable concealer plate/lug position and a nominal pressure difference between tunnel and plenum box of 1.3 Pa (considered most favourable conditions possible)
Result used as ‘baseline’ Special
Deviation of sprinkler set-up from Test 1
2 Frame arms rotated 90 degrees, maximum recess distance, unfavourable concealer plate retainer/lug position and a
nominal pressure difference between tunnel and plenum box of 1.3 Pa (considered least favourable conditions possible)
99.7% increase
3 As Test 1, but with 10 ml of water placed in the concealer plate 256.1
4 As Test 2, but with the vent holes in the sprinkler cup housing blocked and no positive pressure differential between the tunnel and the plenum box 414.6 Off scale
5 As Test 1, but with the concealer plate retainer lugs superglued 6 87.8
6 As Test 1, but with the concealer plate retainer lugs glued with araldite 246.3